gs5556 said:
Connect that ground to where the house ground and lightning ground are connected thereby creating a star ground. This way the voltages across the ground rods will be the same in the event of a lightning strike.
gs5556,
I stand corrected. The lightning electrode system shall be connected, bonded, to the grounding electrode system of the electrical service.
Q. Please explain how I’m supposed to ground a service on a building that has a ground ring used for the lightning protection system grounding electrode?
A. If a lightning protection system is installed on a building/structure, it must be bonded to the building/structure grounding electrode system as per 250.106. The grounding electrode for a lightning protection system must not be used as the required grounding electrode system for the buildings or structures [250.60].
http://ecmweb.com/qampa/code-qa-grounding-lightning-protection-system
//
Principles of Grounding of Lightning Protection Systems per NFPA 7803.
Grounding
A. There are several types of lightning grounding, used separately or in combination, as selected by the installation contractor. Ground rods, perimeter (ring) bare wire, radials, plates, and concrete (rebar) encased designs all constitute acceptable earth electrodes. The lightning grounding electrode is a dedicated part of the lightning protection system. No other ground shall be used as a lightning ground (see section 4.13.1.3).
B. Other (non-lightning) systems requiring grounding shall be integrated (bonded or connected) to the lightning ground to form a common ground potential (see section 4.14). This is to protect electrical equipment from voltage rise mismatches where separate grounds are employed. Under lightning attachment conditions, the lightning ground will function independently of any other grounds. Should electrical system grounds not be connected to the lightning ground, the overall lightning protection system will still function as designed.
http://lightningsafety.com/nlsi_lhm/grounding_principles_NFPA780.html
For the US anyway, per NFPA780 as well as NEC 250.106 and 250.60.
If my understanding is correct each grounding electrode system shall have its own grounding electrode/s. The two systems are then connected, bonded, together. I assume by a minimum #6awg copper wire. In other words lightning rods cannot be installed and directly connected to the electrical service grounding electrode system. Is that your understanding as well?
Jim
.