#10 is used for 30amp breakers and the receptacles for those are 240 not your standard 120 and are made to accomodate #10 wire. Some components are 240 so in that case they would run 10/2 or 10/3.
Am I hearing things?
I just an extra new dedicated line run beside the other one. with 10 gauge wire, 30 amp breaker and a 20 amp rated outlet. I don't think it sounds as good!!! What the hey. A little shrill in both vinyl and CD. I'm comparing from what it sounded like last night. Does electricians wire, breaker and outlet have to burn in? Am I alone in this. I'm have a whole system AC but in and the temp got up to 80. Maybe that is why. Also I'm listening at 11 am EST. So the power grid may have an affect. Did I just answer my own question or have other people experienced this. The original dedicated line was put in in 03 with 12 gauge wire, 20 amp breaker and a 15 amp outlet. Are these 2 lines picking up interferrence?
- ...
- 50 posts total
blueranger OPCall him back and ask him to cite the section in the NEC code that said he can use a 25 amp breaker where a 5-20R (20 amp) duplex receptacle is installed on a branch circuit. Have him look at NEC 110.3 (B) 210.21 (B) (3). Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21 (B) (3), ...... Table 210.21(B)(3) Circuit rating (Amperes) ............Receptacle rating (Amperes) 20 amp ............................................... 15 or 20 amp 30 amp .................................................. 30 amp If you have had problems with nuisance tripping with a 20 amp breaker I would suggest the electrician check and see if the Electrical Panel manufacturer makes an HM (High Magnetic) circuit breaker. An HM breaker has a longer lag time for inrush current. In an earlier post I asked you a few questions. The questions asked relates to the problems you are experiencing with the sound from your audio system, when connected to the new dedicated circuit. . |
- 50 posts total