In the USA Belden 83803 is not approved for branch circuit power wiring per NEC (National Electrical Code).... As far as the manufacture specs, it is designed and UL approved for Power Limited Fire Alarm, (PLFA Class 3)wiring.
NEC 760.121 (A)(1), (A)(2), or (A)(3)
My only reason for pointing out the Belden cable is not approved for branch circuit power wiring is for the OP's and others benefit..... If the cable is used in a manner it is not intended as well as not Listed, approved, and for what ever reason there was a fire or personal injury an insurance claim could be denied by the insurance company.
.
You might ask where in a fire alarm system would #12 wire be used? Horn, or Horn/Strobe circuits...
NEC 760.121 (A)(1), (A)(2), or (A)(3)
My only reason for pointing out the Belden cable is not approved for branch circuit power wiring is for the OP's and others benefit..... If the cable is used in a manner it is not intended as well as not Listed, approved, and for what ever reason there was a fire or personal injury an insurance claim could be denied by the insurance company.
.
You might ask where in a fire alarm system would #12 wire be used? Horn, or Horn/Strobe circuits...