toddverrone OP 121 posts 02-20-20172:26pmIt’s good the outer jacket of the cable is PVC . At least for the way you are using the cable it gives a little better physical abuse protection.
@jea48 check this:
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet393
That is the wire I used. The outer jacket is high temp smokeless PVC and the individual wire insulator is FEP or what is commonly referred to as Teflon. I promise I did my homework
Yes, it says the insulation cover for each 24 gauge wire is FEP. Though if you scroll down the page it says the insulation is thermoplastic, which is PVC. I wonder if it is thermoplastic with a layer of Teflon over that?
toddverrone OP 121 posts 02-20-2017 10:39am
I promise, if you do the research you can confirm, cat 5 that is UL listed is rated to 300v
Yes, you are correct. But at very low amperage, rated in ma. Example, the ringer voltage on a telco phone system. The voltage on the ringer circuit can averages around 90 volts AC. It can go as high as 140Vac, possibly 150Vac. But the current is very low in the ma range. The circuit is also fuse protected which limits the current.
Again the cat5e cable was never designed/tested/manufactured/UL Listed to be used as a mains 120Vac power cord. If for what ever reason the cord faulted the current available from your electrical panel could be in the hundreds of amps before the branch circuit breaker could react and hopefully trip open breaking the fault. Will all the paralleled #24 gauge wires survive the event? What limiting fuse protection do you have to protect the parallel 24 gauge wire of the power cord?
If the fault is an arcing fault the breaker will never trip as long as the continuous current draw is below the breaker handle rating. Of course the same is true for any power cord. One reason for NEC code AFCI (Arc Fault Circuit Interrupter) branch circuit protection.
Bottom line..... You feel safe with the power cord you have assembled. The PVC outer jacket on the cat5e helps. I personally would not build a power cord using cat5e data cable. I would also not recommend anyone reading this thread do so either.
.