Time for dedicated outlets!


I would like some advice on what exactly to tell my electrician to be sure I get what I need. Is just saying that I want two separate dedicated lines to the listening room sufficient or are there other key fraises that should be included in my description of the work I would like done?
mizike
10-3 was used for greater distance. My nextdoor neighbor who is a electrician ran that. So I have 2 20amp. At the wall we put 2 sets of outlets each set is on a separate breaker


Outlet. Outlet. Outlet Outlet
Outlet. Outley. Outlet Outlet
     1.          2.         1.        2
Breaker Breaker Breaker Breaker


It is this way so I can decide how much load is on each beaker.
Why are you guys using 10/3 Romex? What are you doing with the extra wire? 10/2 Romex has 2 insulated conductors and a bare ground. 10/3 has 3 insulated conductors and a bare ground.  Maybe you guys are confused about the wire naming? If not, I'm so curious what that extra wire is for!
Baddoge, if u have four breakers u have four circuits and u did not get that with 10/3 wire. 10/3 wire has 2 hots a neutral and a ground and is good only for 2 circuits. You must have run more wire
That's a violation of the NEC

I'm assuming NEC is an American standard @cleeds ?
bumperdo, you need to read cleeds post above. A separate ground on the sub-panel is contrary to the NEC.