mental522
@djones...you are very mistaken, he’s running two circuits using the same neutral. Two single pole breakers should be used, one for each circuit. A double pole breaker is designed to use different phases, all he has to do is put the single poles back in where the double pole is. I suggest you stop giving out electrical information, you are clueless.
@mental522
The National Electrical Code permits multiwire branch circuits, but adds requirements to make them safer. Section 210.4(B) states that in the panelboard where the branch circuit originates, all ungrounded conductors must be provided with a means to disconnect them simultaneously. This is usually a double-pole breaker, but two single-pole breakers may be used if they have an identified handle tie.https://www.jadelearning.com/multiwire-branch-circuits-nec-210-4/
Mike Holt on multiwire branch circuit
https://www.youtube.com/watch?v=_VjZ5ySblew