Dealing with a power amp that need 20A connection


I just bought a used Audio Research power amp without knowing it needs 20A connection.
When I received the amp, there was no power cable included, and I've found out that the amp has a connection that I've never seen before. I thought it might be for 250 Volt, but later found out that this amp needs a special power cable with C19 type female connector and it has to be 12 AWG and 20A.
So, I ordered a 20A 12AWG power cable and a PS Audio power receptacle that supports 20A male connector type.
After reading a few more articles on 20A power amp, I may also need a 20A circuit breaker. The problem is, the circuit breaker for the audio room is 15A. Does it mean that I need a new breaker with 20A to use the amp?
What a hassle.
The seller did not mention anything about the cable power requirement and I assumed that it was included, but the seller didn't seem to have known anything about this amp. 
So, installing a new circuit breaker is something non tech people can do? If not, how much would I need to spend for professional job?
Would it be just OK to use 15A circuit breaker for the amp as long as I use 20A 12AWG power code and don't turn the volume much high?
Thx advance for your input.
128x128ihcho
I contacted ARC service and asked a question about this amp over two weeks ago, but no response yet.
Most of time, it is more responsive and sometimes more detailed response I get from online forum than the manufacture's customer service. 
So far so good at moderate volume (9 o'clock position).
@ ihcho

Did you read page 2 of the 150M owner manual?

Either ARC had a lawyer write it, or ARC just stopped some guy off the street to write it.

Quote from page 2.
The AC power source for the amplifier should be capable of supplying 15 ampere for 100 or 120 volt units,
Yeah, really? 15 amperes..... I wonder how many layman read that as a 15 convenience outlet circuit meets that statement?
I can tell you how the majority of electricians would read it. The equipment manufacturer says his piece of equipment needs a 120Vac 20 amp circuit.

Here’s the thing though. Technically ARC meets UL, and NEMA safety standards. It is also in compliance with NEC electrical code. The continuous (repeat continuous) FLA of the amplifier is not greater than 12 amperes. That complies with NEC, UL, and NEMA, electrical safety standards for a 15 circuit.

And then in the next paragraph it says;
For the very best performance on domestic 100 or 120 volt circuits the 150M should be connected to its own AC power circuit branch protected by a 20 amp breaker.

its own AC power circuit branch protected by a 20 amp breaker.
Normally it would be worded, 20 amp branch circuit. Per NEC the overcurrent protection device, breaker in this case, determines the size of the branch circuit.
For a 20 amp branch circuit the bare minimum branch circuit conductor, wire, size is number 12awg. You can go with a bigger size, but not smaller than #12awg.

So why all the dancing around the branch circuit size ARC recommends for the amplifier? The vast majority of homes in the US convenience outlet circuits are 15 amp. (15 amp breaker, #14awg wiring). Living rooms, bed rooms, dens.
Jim


I also have read that statement: 
For the very best performance on domestic 100 or 120 volt circuits the 150M should be connected to its own AC power circuit branch protected by a 20 amp breaker.

That's why I thought about having a dedicated 20A circuit for this amp.
However, so far it seems to be fine with 10awg 15A power cord.  
As I said before, doing it the 'right' way would be the safest course, and probably give you a better outcome overall, but, I think running it with an adapter is fine as long as you don't push it.
Even if you do, the breaker should kick in, and then you'll know how far you can go.
B
Jim, I'm curious to hear your thoughts on pig-tailed vs. daisy-chained wiring of outlets, if you have the time. Not necessarily per audio requirements, but in general.
TIA