DC Offset Blocker/Killer - where to buy in the USA


   I have McIntosh MC8207, the first unit I bought from an authorized dealer came with a loud buzzing coming from the left transformer, and was replaced with a new unit which came with even a louder buzzing. The buzzing can be heard from 8 feet away. Then I was told to have install new 20 amp outlet that has its own isolated grounding.
   That was done professionally by an electrician who installed two isolated 20 amp outlets, two 20 amp circuit breakers, two copper polls for grounding for each outlet, each outlet has its own neutral and power line. After all this done the buzzing sound was still there.
   I was then told to buy a power conditioner which I did (Audio Quest Niagara) which was like $4000 and that did not help. Called back McIntosh and was told that I might have DC offset in my AC line and was told by McIntosh that I would need a DC Offset Blocker/Killer to which when I asked them where to buy one they told me to go on the internet and search to find one, to which I cannot find one.
  This bothers me a little bit, if you as a company think that I have dc in my ac and i need a dc blocker wouldn't you need to sell one as well. I brought this amp to my friends house and it was the same no improvement, so my guess is that he has dc in the ac line as well.
   So If anyone of you knows where to buy a DC Offset Blocker/killer please let me know, but even if this helps kill the buzzing wouldn't you guys think that this expensive somewhat hifi amp/brand should be silent from the factory. I mean this is two units in a row all purchased brand new.

My house is 5 years old, everything is brand new, the whole neighborhood is about 8-9 years old, my electrician says that I have perfect power coming to the house and everything looks fine.

Thank You

tomiiv30
@tomiiv, 
Good Move.
There are plenty of great amplifier designers out there that you can choose from.
Especially at that price point.
Bob
It's a story as old as the hills.

A company spends decades establishing a really good name.

A conglomerate swoops in and buys it up--and they're buying the name much more than the factory or the know-how.  They proceed to try and squeeze every last drop of profit out of it--and then they'll throw away the dry husk when they're done.

The attitude you've gotten--it's your problem, we really don't want to take it back (=we've already made our profit off of you)--is a classic demonstration of this.
@twoleftears ,
Exactly.
I bought a 2016 TTS that has a B&O sound system. 
It sounds like crap. My previous TTS had a Bose system that sounded leaps and bounds above the B&O-and that is saying something.
B&O had some really interesting gear in the day, but now that they have been acquired by another company, they are just resting on the name recognition.
Too bad for me, Audi trusted them- but, hey, it all comes down to money.
B
Food for thought.
Quote from an Audio Circle audio forum thread about DC offset on the AC mains.
HAL
  • Industry Contributor


  • Posts: 4101



Re: DC offset on AC line « Reply #8 on: 30 Nov 2007, 03:51 am »


 
If you have access to a Fluke 43B power line analyzer, you can check the harmonic distortion on the AC line. Had a similar problem with lots of audio gear in the house. Turned out the the AC line harmonic distortion was running about 6%.

The local power company did some investigation. Found out the meter base contacts had corrosion. After clean up, the AC line distortion runs about 2%.  No more power transformer hum.
https://www.audiocircle.com/index.php?topic=47973.0

.
https://www.diyaudio.com/forums/solid-state/2080-dc-filter-6.html#post331815


22nd February 2004, 08:09 PM
  #57 Eva   diyAudio Member  
 
Join Date: Oct 2003 Location: Near the sea


 
I've done some measurements that show what's really hapening when you connect a transformer to mains

Using a lowpass filter [100k + 47uF] I have measured about 50mV average over time of DC on my mains supply

I also have an old electric heater that in half-power mode uses a diode in series with the heat element to pass only half of the mains waveform. When I plug this heater in half-power mode I get an additional 1V of offset on mains supply

To test the need and the efficiency of DC filtering, I've done some measuremens of the current through the primary of a 750VA toroidal transformer

This oscillogram shows what happens when I connect the transformer to mains and let it deal with the 50mV DC offset

An externally hosted image should be here but it no longer works. Please upload images instead of linking to them to prevent this.

Blue trace is mains waveform at 100V/div [230V AC], it looks more like a clipped triangle wave instead a sine wave due to the line inductance limiting the slew rate and all the rectifiying applications consuming all the current only during the peaks [30% of total time]

Red trace is the current through the primary at 200mA/div. Transformer saturation towards the negative side is evident, reaching 350mA peak of leakage current. The transformer buzzs slightly due to the saturation

The noise present in the current waveform is common mode and was suppressed in further measurements adding a common mode filter between mains and measurement point


The second oscillogram shows what happens when I plug the electric heater in half-power mode

An externally hosted image should be here but it no longer works. Please upload images instead of linking to them to prevent this.

Red trace this time is in 2A/div so the leakage peak current exceeds 6A. The transformer is heavily saturated towards the upper side and buzzs loudly.


The third oscillogram shows what happened when I placed a DC filter consisting of two 1000uF 16V and some diodes in series with the primary

An externally hosted image should be here but it no longer works. Please upload images instead of linking to them to prevent this.

This time, red trace is 20mA/div and shows the small leakage current due to both the magnetizing inductance and the parasitistic capacitance between adjacent turns. The transformer is no longer saturated and performs silently


the fourth oscillogram shows the induced voltage in a loop of wire of 10cm diameter placed vertically, paralell and 1cm away from the transformer [placed horizontally] obtained when the transformer was saturating with more than 6A peak [with the electric heater plugged]

An externally hosted image should be here but it no longer works. Please upload images instead of linking to them to prevent this.

The red trace is 2mV div and shows the induced voltage in the loop of wire

That measurement demonstrates that when a 50-60Hz transformer is saturating, it produces electro-magnetic-interferences that induce noise voltages on everything in the nearhood

Actually, I think that +-5mV of low frequencies induced in a loop of wire of 10cm diameter near the transformer is a serious thing since this EMI is at audio frequencies, it's not RF so it's 100% audible and it may be happening in all your transformers

In the other hand, all the tests were performed with open secondaries but if we add load so that primary current has peaks of 6A, then the EMI radiated would be the same or higher

With load, the EMI is produced due to flux in the leakage inductance, resonances due to parasitistic inter-turn capacitance, RF ringing due to diode turn-off characteristics and the fact that the peak current through the transformer is 3 times or more the average DC current after rectification

In conclusion : Rectifiying the output of 50-60Hz transformers produces EMI as any SMPS does and this phenomena gets aggravated when the transformer is saturating due to direct connection to mains without a DC filter

50-60Hz transformers are nothing but big, bulky and crappy antennas
 
https://www.diyaudio.com/forums/solid-state/2080-dc-filter-6.html#post331815

.



22nd May 2004, 05:20 PM   #71 Eva   diyAudio Member  
 
Join Date: Oct 2003 Location: Near the sea





Bricolo :

DC levels on mains cannot be measured by directly connecting the multimeter to the line. You have to place a low-pass filter between the line and the DMM. I use a first order filter made of a 100K 1W resistor and a 22uF non-polar capacitor for that purpose

Non-gapped transformers must be operated on 'pure AC'. Even 50mV of DC may be enough to see signs of saturation on toroids
 



.