Dedicated 20 amp lines/should i use a sub panel


Happy New Year to all!!

I am about to install 3 - 20 amp dedicated lines for my stereo. I still have space in my 200 amp main panel but was wondering if their is any benefit to installing a 60 amp sub panel for the 3 audio circuits , also as i am using 10 gauge wire and its not the easiest to manipulate should i hook up the bare wire to the receptacles looped around the screws or inserted in the holes or should i use spade connection's. any advice would be appreciated.

Thanks in advance
Chris 
spinner1
Jim, Some replies below.

By side by side, do you mean the breakers are installed directly across from one another? Connected to the same main bus breaker tie. (Both are fed from the same leg, Line.) Or, do you mean one is installed above the other, side by side? One fed from leg, Line 1 and the other fed from Leg, Line 2?
>>> Same leg/busbar. One 20A breaker above other.

Did you use Romex?
>>> Yes. 8/2 NM-B (not 10 as I said before) cable from Lowes.

Did you try to keep the 2 cables separated from one another at least 6" after getting them out of the electrical panel, as soon as practical? Especially a long parallel run?
>>>Yes. 12 feet apart.

Is it possible one of the 2 is running parallel next to some other branch circuit?
>>>It’s possible but not obvious.

>>>I also tried tying the ground wires to the same terminal, removing the ground (to test only) and moving other equipment to different runs to no avail. I’ll be honest, I abandoned messing around with it after an hour and removed one leg and used the cable for another project. The one 8/2 run on a 20A breaker into a 20A L5-20/L5-20P receptacle/plug sounds great.
noromance
901 posts                                                                     01-04-2018 12:07pm

Jim, Some replies below.

By side by side, do you mean the breakers are installed directly across from one another? Connected to the same main bus breaker tie. (Both are fed from the same leg, Line.) Or, do you mean one is installed above the other, side by side? One fed from leg, Line 1 and the other fed from Leg, Line 2?
>>> Same leg/busbar. One 20A breaker above other.

>>>
Same leg/busbar. One 20A breaker above other.
If the breakers are directly above one another, there in on the same side of the electrical panel, they are not fed from the same leg/bus bar. (For standard size single pole breakers.) One is fed from one leg, Line, and the other is fed from the other Leg, Line.

You can easily verify this with a multimeter.
Insert one test probe in the Hot contact of an outlet fed from one dedicated circuit and the other test probe in the Hot contact of the other dedicated circuit outlet.
~ If both are fed from the same leg, Line, bus bar, the meter will measure zero volts.
~ If the meter reads 240V, nominal, then one circuit is fed from one leg, Line, and the other circuit is fed from the other leg, Line.

Did you use Romex?
>>> Yes. 8/2 NM-B (not 10 as I said before) cable from Lowes.
8-2 with ground? Not 8-3 with ground?

Jim

Besides having built-in noise cancelling features, and surge protection, another advantage to the sub-panel is that you end up with a star grounding scheme that is short, and therefore much less likely to cause differences in ground potential.

The biggest source of noise in my mind is usually other household appliances, and dimmer switches. If you get separate runs, without any noise cancelling, you are literally just making it easier to pick up noise from anywhere in the house. Having a 30 to 60 Amp subpannel that has its own noise and surge protection is the key.

Best,

E
Jim,
8/2 with ground. You are correct about the legs. I also tried it on both legs. So instead of 22, 24, where I originally connected it, I had tried it on 23, 24 but it still hummed. In fact, as it’s a basement space, I just ran in a 12/2 on 15A breaker on the same leg to see if it still hummed with the (2 wire) monos. It did. But it doesn’t when I add my REL sub. So all is not lost! I should say that there is normally no hum from the rig.
How far away is the main panel from your listening room? If it’s more than 50 feet then it pays to put in a subpanel since a branch circuit of that distance will have a high voltage drop (3 volts with #12 and 1.8 volts with #10 at a 15-amp peak draw).

If distance is not an issue, use 10/3 romex because the wires are spiraled and that reduces common mode noise. Cut the bare grounding conductor and use the red wire for ground (tape it green where exposed, of course). Also, use the clamps under the screw of the receptacle for #10 wire instead of looping it around the screw. And use 10/3 from the subpanel to the receptacle also.