Jim, Some replies below.
By side by side, do you mean the breakers are installed directly across from one another? Connected to the same main bus breaker tie. (Both are fed from the same leg, Line.) Or, do you mean one is installed above the other, side by side? One fed from leg, Line 1 and the other fed from Leg, Line 2?
>>> Same leg/busbar. One 20A breaker above other.
>>>
Same leg/busbar. One 20A breaker above other.If the breakers are directly above one another, there in on the same side of the electrical panel, they are not fed from the same leg/bus bar. (For standard size single pole breakers.) One is fed from one leg, Line, and the other is fed from the other Leg, Line.
You can easily verify this with a multimeter.
Insert one test probe in the Hot contact of an outlet fed from one dedicated circuit and the other test probe in the Hot contact of the other dedicated circuit outlet.
~ If both are fed from the same leg, Line, bus bar, the meter will measure zero volts.
~ If the meter reads 240V, nominal, then one circuit is fed from one leg, Line, and the other circuit is fed from the other leg, Line.
Did you use Romex?8-2 with ground? Not 8-3 with ground?
>>> Yes. 8/2 NM-B (not 10 as I said before) cable from Lowes.
Jim