You say a 7.5kva xfrmr. 230 volt primary 120 volt secondary? If it is indeed 120v out your electrician will bond one leg of the secondary to ground. This will become the grounded conductor and will terminate on the neutral bar of your new electrical panel. The electrician will bond the neutral bar to the panel enclosure with the supplied bonding screw. For the grounding, do you have a metallic water service, copper? This will be your primary ground electrode. Run a #6 awg min cu wire from the new elect panel neutral bar to a new water pipe clamp installed on the water pipe ahead of the water meter. Clean the water pipe with sand paper to a brite copper like new look. This #6 awg wire is called the grounding electrode conductor. While your electrician is at the meter location have him clean up your main service ground clamps and water meter jumper wire. Next ground to run is the secondary grounding electrode conductor. Not knowing where you live and the type of soil and moisture you have your electrician should know best. Drive two 10ft ground rods out side your house, at least 6ft apart at least 10ft 4" deep. Run a #6 awg min cu wire from the neutral bar of your new elect panel to these new ground rods.For these rods try to pick an area closest to your new panel. Your electrician will know the proper procedure for bonding the wire to the rods this can vary in areas due to local codes. Note, If the electrician feeds the 7.5kva xfrmr with romex run #10-2 w/grd awg cu min. Ground the case of the xfrm from your main house service panel. If the xfmr should have a short the fault current will travel back on this equipment grounding conductor and cause the breaker feeding the xfmr to trip open. With this xfmr you are creating a new seperately derived ac system. In the new panel board install a single pole 60 amp breaker for the main breaker. I recommend Square D QO panelboard and breakers.
Hope this will help.
Hope this will help.