Electrician specializing in audio needed Buffalo


I am looking for an electrician specializing in audio installations in the Buffalo, New York area. Please respond if you can recommend someone. Thank you.
tmmvinyl
There must be some Local 41 guys looking for some extra cash from side jobs; do you see anything in the buffalo evening news or any of the bee magazines (Amherst,clarence,etc...) Maybe the guys at the speaker shop on main street can give you some contact names to try.
Rleff,

Thank you for suggesting the Speaker Shop; I hadn't thought about them. I have spoken with a number of electricians but none of whom have any real audio-specific experience.
I have spoken with a number of electricians but none of whom have any real audio-specific experience.
Tmmvinyl
You really don't need an electrician that is audio savvy.
You just need to do your homework and write up a set of specs you want him to follow. The electrician will look at the specs then he will tell you what he can do and cannot do to meet code in the state and city you live in.
The electricians in your area will know the local codes for your area.

Example, he may not be able to use/install NM-B sheathed cable, (Romex is a trade name for NM-B), by code in your area for branch circuit wiring. The wiring may have to be installed in metallic conduit. If that is the case ask him if aluminum armor MC cable meets code. If so have him use AL armor MC cable with solid core conductors. Three wire, hot, neutral, and green insulated equipment ground. One MC cable for each dedicated branch circuit you want.

Avoid pulling branch circuit wiring in an empty installed conduit. Avoid installing a dedicated branch in a conduit with other branch circuits.

Pay close attention to pages 31 through 36
An Overview of Audio System
Grounding and Interfacing


If you are wanting more than one dedicated circuit spec all circuits to be fed from the same Line, leg, in the electrical panel. All from Line 1 or all from Line 2, but not from both.

Jim
Jim, thank you for responding.

I have two separately metered services into my home. One service is solely dedicated to my listening room. The panel sits directly beneath my listening room. I have 5 dedicated runs of solid 10 AWG wire from 20 amp breakers to 5 in-floor Furutech duplex outlets. The longest run of wire is 11 feet. All wiring is fully exposed and none of it travels through the wall. Getting this work done, required three different electricians, not one of whom had any interest in listening to me or in following my instructions. I am now looking for someone who can properly ground my installation because I am still dealing with a fair bit of hum.