For a test did you ever try connecting all the audio equipment to just one dedicated circuit's duplex receptacle and check for the hum you are hearing? You might want to try that first.
5 separate runs of what type of #10 wiring?
Romex?
MC cable?
Conduit/s with #10 wires pulled in the conduit/s?
Hopefully you can see 5 individual home runs, one for each dedicated 120V circuit.
Are all 5 circuits connected to same Line, leg, in the electrical panel?
Best way to check is with a multimeter and measure for voltage from one duplex receptacle to one of the other duplex receptacles. Insert one test lead probe in the hot contact, small blade slot, of one of the receptacles of a duplex and the other test lead probe in the hot contact of one of the other duplex receptacles. You should read zero volts. Repeat the process from the first duplex receptacle to the remaining three. If you measure 240Vac nominal on any of the 5 circuits they are not all fed from the same line in the electrical panel.
If you do not have a volt meter you can try this. Go to the electrical panel where the 5 circuits are fed from.
I assume the electrical service is 120/240V single phase.
Check the panel circuit breaker numbers.
L1 > 1 .... 2 < L1
L2 > 3 .... 4 < L2
L1 > 5 .... 6 < L1
L2 > 7 .... 8 < L2
L1 > 9 ... 10 < L1
L2 > 11 .. 12 < L2
The 5 circuits should all be fed from L1, or, all fed from L2. They should not be fed from both.
Wow, an electrician/s that don't listen to the person that hired them and is paying them.
You need to find an electrical contractor that will work with you. With that said he has to follow electrical codes for Buffalo.
You might try giving the IBEW Electrical workers Local 41 a call and ask to speak with the Business manager or his assistant manager. Explain to him your problem and ask him if he can recommend an electrical contactor that will work with you instead of the other way around.
Phone: 716-662-6111
.
Jim
5 separate runs of what type of #10 wiring?
Romex?
MC cable?
Conduit/s with #10 wires pulled in the conduit/s?
Hopefully you can see 5 individual home runs, one for each dedicated 120V circuit.
Are all 5 circuits connected to same Line, leg, in the electrical panel?
Best way to check is with a multimeter and measure for voltage from one duplex receptacle to one of the other duplex receptacles. Insert one test lead probe in the hot contact, small blade slot, of one of the receptacles of a duplex and the other test lead probe in the hot contact of one of the other duplex receptacles. You should read zero volts. Repeat the process from the first duplex receptacle to the remaining three. If you measure 240Vac nominal on any of the 5 circuits they are not all fed from the same line in the electrical panel.
If you do not have a volt meter you can try this. Go to the electrical panel where the 5 circuits are fed from.
I assume the electrical service is 120/240V single phase.
Check the panel circuit breaker numbers.
L1 > 1 .... 2 < L1
L2 > 3 .... 4 < L2
L1 > 5 .... 6 < L1
L2 > 7 .... 8 < L2
L1 > 9 ... 10 < L1
L2 > 11 .. 12 < L2
The 5 circuits should all be fed from L1, or, all fed from L2. They should not be fed from both.
Getting this work done, required three different electricians, not one of whom had any interest in listening to me or in following my instructions. I am now looking for someone who can properly ground my installation because I am still dealing with a fair bit of hum.
Wow, an electrician/s that don't listen to the person that hired them and is paying them.
You need to find an electrical contractor that will work with you. With that said he has to follow electrical codes for Buffalo.
You might try giving the IBEW Electrical workers Local 41 a call and ask to speak with the Business manager or his assistant manager. Explain to him your problem and ask him if he can recommend an electrical contactor that will work with you instead of the other way around.
Phone: 716-662-6111
.
Jim