P=IxE
P= power,watts,VA
I= current,amps
E= voltage
NEMA 5-15R, 15 amp receptacle, two or more can be on a 20 amp breaker. Wire size #12 or larger.
Maximum continuous full load current on a single nema 5-15R receptacle is 12 amps.
Maximum continuous full load current on a sigle NEMA 5-20R is 16 amps.
Maximum overcurrent device, breaker, for a NEMA 5-20R is 20 amp.
This is according to NEC, National Electrical Code.
This also parallels UL standards.
A 20 amp cord cap,NEMA 5-20P plug, has one vertical straight blade, the hot ungrounded conductor.The other straight blade is horizontal,the neutral, the grounded conductor.This would be looking at the wall with the ground prong down.Hot on the right, neutral on the left.
30 amps, no way on a NEMA 5-15P. I just can not believe it could get a UL listing.