Audiolover718,
Depends on your circumstances.
How big is the ARC amp? What is the ARC model number?
What size is the branch that feeds the amp? 15 amp? 20 amp?
What is the length of the branch circuit wiring from the panel to the outlet receptacle the preamp and amp are plugged into?
How many other duplex receptacles and possibly ceiling light fixtures are connected to the same branch circuit your preamp and amp are plugged into? What was the wiring method used to wire the receptacles that feed onto the next receptacle of the branch circuit? Wiring daisy chained using the duplex receptacles to make the in and out wiring connections of the branch circuit wire? Corroded/loose/poor connections add resistance to the circuit. The more the load placed on the circuit the greater the VD, voltage drop. How much is the other non audio connected load connected to circuit?
All the above can affect how a piece of audio equipment will preform. Branch circuit breakers are designed to trip open in the case of a continuous overload condition, a high sustained inrush current condition well over the handle rating of the breaker, or a short circuit event.
The breaker does not respond to short bursts of current passing through it. Example, a 15 amp branch circuit, 15 amp breaker with #14 awg copper wire connected to it, will easily pass short bursts of current well over its handle rating of 15 amps all day long. The breaker could care less what is causing the short spurts of current that is passing through it over its' 15 amp handle rating. It also could care less if the voltage at the receptacle feeding the preamp and amp is fluctuating up and down due to VD, voltage drop, caused by bursts of current placed on the #14 awg wire.
The power supplies of a preamp and power amp might though. Power amp's power supplies like its' mains voltage to be steady and not fluctuating with the beat of a high dynamic music source being fed through it.
.
Jim
Depends on your circumstances.
How big is the ARC amp? What is the ARC model number?
What size is the branch that feeds the amp? 15 amp? 20 amp?
What is the length of the branch circuit wiring from the panel to the outlet receptacle the preamp and amp are plugged into?
How many other duplex receptacles and possibly ceiling light fixtures are connected to the same branch circuit your preamp and amp are plugged into? What was the wiring method used to wire the receptacles that feed onto the next receptacle of the branch circuit? Wiring daisy chained using the duplex receptacles to make the in and out wiring connections of the branch circuit wire? Corroded/loose/poor connections add resistance to the circuit. The more the load placed on the circuit the greater the VD, voltage drop. How much is the other non audio connected load connected to circuit?
All the above can affect how a piece of audio equipment will preform. Branch circuit breakers are designed to trip open in the case of a continuous overload condition, a high sustained inrush current condition well over the handle rating of the breaker, or a short circuit event.
The breaker does not respond to short bursts of current passing through it. Example, a 15 amp branch circuit, 15 amp breaker with #14 awg copper wire connected to it, will easily pass short bursts of current well over its handle rating of 15 amps all day long. The breaker could care less what is causing the short spurts of current that is passing through it over its' 15 amp handle rating. It also could care less if the voltage at the receptacle feeding the preamp and amp is fluctuating up and down due to VD, voltage drop, caused by bursts of current placed on the #14 awg wire.
The power supplies of a preamp and power amp might though. Power amp's power supplies like its' mains voltage to be steady and not fluctuating with the beat of a high dynamic music source being fed through it.
.
Jim