Edit for previous first post dated 03-03-15: Jea48
NEC Code
210.21 (B)(3) Receptacle Rating.
Where connected to a branch circuit supplying two or more receptacles or outlets, receptacles ratings shall conform to the values listed in table 210.21(B)(3), ...........
NEC Table 210.21(B)(3) Receptacle Ratings for Various Size Circuits.
Circuit Rating ..... Receptacle Rating
(Amperes) .............. (Amperes)
15 ............................ 15
20 ....................... 15 or 20
30 ............................ 30
Minimum wire size #10awg. Breaker size 30 amp.
*No exception given for Krell Inc.
>>>>>>>>>>>>>>>>>>>>>>>
Strike,
and replace with,
The branch circuit breaker size determines the size of the branch circuit.
If the branch circuit breaker is 30 amp then the minimum wire size must be #10 AWG. It can be bigger but it cannot not smaller.
The receptacle must be a NEMA 125V 30 amp rated receptacle. It cannot be bigger, it cannot be smaller, it can only be a NEMA 30 amp rated receptacle.
.
NEC Code
210.21 (B)(3) Receptacle Rating.
Where connected to a branch circuit supplying two or more receptacles or outlets, receptacles ratings shall conform to the values listed in table 210.21(B)(3), ...........
NEC Table 210.21(B)(3) Receptacle Ratings for Various Size Circuits.
Circuit Rating ..... Receptacle Rating
(Amperes) .............. (Amperes)
15 ............................ 15
20 ....................... 15 or 20
30 ............................ 30
Minimum wire size #10awg. Breaker size 30 amp.
*No exception given for Krell Inc.
>>>>>>>>>>>>>>>>>>>>>>>
Strike,
Minimum wire size #10awg. Breaker size 30 amp.
and replace with,
The branch circuit breaker size determines the size of the branch circuit.
If the branch circuit breaker is 30 amp then the minimum wire size must be #10 AWG. It can be bigger but it cannot not smaller.
The receptacle must be a NEMA 125V 30 amp rated receptacle. It cannot be bigger, it cannot be smaller, it can only be a NEMA 30 amp rated receptacle.
.