ground the outlet or not??


Guys - I have the Equi-tech cabinet mount power center with an earth ground- I am about to install the Furutech NCF outlets and someone mentioned to me that I should NOT hook up the ground wires to the Furutech outlet- Just cut it off before the  outlet box-box- Does this make sense or not - thks
fluffers
Also jea48, I read both your post,  I agree whole heartily! , great read, I will tell you all here,  what jea48 posted here is code,  and the truth , especially concerning the op's topic post. 
Makes no sense whatsoever. What the Equi-Tech does is supply power in the same manner as a 2-pole 240 volt circuit only at 120 volts. You still need the grounding conductor on 240 volt outlets as Jea48 nicely summarizes the code and safety issues.

Before you hook up balanced 120 volt to your equipment, I would check with the manufacturer to see if they have any warranty objections. With balanced 120v there are now two current carrying conductors, so there should be a fuse on the equipment mains neutral as well as the hot. If you look at amplifiers with split primary power transformers (to operate at 120 or 240 volts) they have two mains fuses. If it runs at 120, only one fuse protects since the neutral is at zero volts but when converted to 240 the neutral is at 120 volts and therefore a short in the amp power supply will draw current from both legs, hence the reason for the second fuse. The same thing will happen with balanced 120, only the potential is 60 volts.

gs5556,

You are forgetting NEC 210.6 Branch-Circuit Voltage Limitations.

Quote from NAPF 70, 2014 NEC

210.6 Branch Circuit Voltage Limitations.

(A) Occupancy Limitations. In dwelling units and guest rooms or guest suites of hotels, motels, and similar occupancies, the voltage shall not exceed 120 volts, nominal, between conductors that supply the terminals of the following:

(1) Luminaires

(2) Cord-and-plug connected loads 1440 volt-amperes, nominal, or less that 1/4 hp.

End of quote.

//

Lots of available power.

15 amp branch circuit/s. 240V x 15 amps = 3600VA, watts.

20 amp branch circuit/s. 240V x 20 amps = 4800VA, watts. Just imagine a home brew power cord plugged into that.

The user more than likely would want to use an audio grade NEMA 5-15R 15 amp 125V rated duplex receptacle/s or a NEMA 5-20R 20 amp 125V duplex receptacle/s so he/she can use his/her after market audio grade power cords.

Jim