The ground system in a home is not for people protection it is for fire protection. If there is current on the chassis and someone touches it the breaker is probably not going kick in time to save someone.
Like Al, (almarg), said you are wrong.
It is for protection of life from electrical shock or electrocution. The equipment ground places the metal cabinet/enclosure of the piece of equipment at the same ground potential as the main electrical service’s grounding system. Any grounded object within the premises is supposed to all be at the same ground plane potential.
If the metal case/enclosure of a piece of equipment is properly grounded any ground fault potential that comes in contact with the enclosure will pass the current through the safety equipment grounding conductor back to the earth connected service neutral conductor. If the ground fault current, plus equipment load, is greater than the breaker handle rating the breaker will trip open breaking the ground fault circuit. If the ground fault has a high series resistance good chance the breaker will not trip open.
The breaker sees the ground fault current as just part of the total connected load.
If the piece of equipment has a safety fuse the fuse should blow first.
(That is if the AC polarity is correct at the wall receptacle and the Hot conductor is connected to the line side of the fuse. If the AC polarity is reversed then the neutral will be connected to the line side of the fuse.) In any event IF a ground fault circuit is provided the current will travel back on the equipment grounding conductor to the earth grounded service neutral conductor. At no time is the enclosure/chassis HOT with respect to ground.
IF the enclosure of the equipment is properly grounded the enclosure is at ground potential and should never have any difference of potential to any other earth grounded object.
.