wgutz,
The lower the Grounding Electrode, ( example, ground rod), to soil resistance the better. IEEE recommends 5 ohms or less, preferably 2 ohms or less.
It’s not the number of ground rods driven into the earth that will necessarily yield a 2 ohm soil resistance. A lot depends on the content/type of soil and soil moisture. Where you live can make a difference. The 4 seasons can greatly impact soil moisture. It is possible a single 5/8" X 20ft driven ground rod will have a lower ground resistance than 6 individual 5/8" X 8ft driven ground rods.
When multiple ground rods are driven into the earth they should all be tied/connected together with a single wire extended and connected to the electrical service entrance neutral conductor. The multiple ground rods then become a single Grounding Electrode.
Harmonics? The earth will not reduce harmonics.
The majority of harmonic noise found on the AC mains in a home are caused by electronic devices found in the home. Seldom will those produced in the neighbor’s house end up adding to the harmonic noise found in your house.
A refrigerator motor does not produce harmonic noise. Now the micro processor that controls the features on the refrigerator can.
Nonlinear loads produce harmonic noise back on the AC mains.
Examples of,
Switch mode power supplies
Light dimmers
Hair dryers
Computers
Variable frequency drive units found on many of the furnaces built today. (Controls blower motor speed)
Dual wattage portable electric space heaters.
CFL and LED lights
Electronic ballasts
//
PS Audio power regeneration units.
Curious, have you ever checked if the outputs of the two units are in phase with one another? If you have a multi meter measure the voltage from the hot contact from one of the output receptacles on one units to the hot contact of an output receptacle on the other unit. If the outputs of the two units are in phase you should measure zero volts nominal. If out of phase you will measure 240Vac nominal.
//
Sub Panel.
Don’t use it to feed your audio equipment. The wire feeding the panel is too small. Use the main electrical panel.
http://www.p3-inc.com/images/grounding_for_pq_wp2016_p3.pdf
.
The lower the Grounding Electrode, ( example, ground rod), to soil resistance the better. IEEE recommends 5 ohms or less, preferably 2 ohms or less.
It’s not the number of ground rods driven into the earth that will necessarily yield a 2 ohm soil resistance. A lot depends on the content/type of soil and soil moisture. Where you live can make a difference. The 4 seasons can greatly impact soil moisture. It is possible a single 5/8" X 20ft driven ground rod will have a lower ground resistance than 6 individual 5/8" X 8ft driven ground rods.
When multiple ground rods are driven into the earth they should all be tied/connected together with a single wire extended and connected to the electrical service entrance neutral conductor. The multiple ground rods then become a single Grounding Electrode.
Harmonics? The earth will not reduce harmonics.
The majority of harmonic noise found on the AC mains in a home are caused by electronic devices found in the home. Seldom will those produced in the neighbor’s house end up adding to the harmonic noise found in your house.
A refrigerator motor does not produce harmonic noise. Now the micro processor that controls the features on the refrigerator can.
Nonlinear loads produce harmonic noise back on the AC mains.
Examples of,
Switch mode power supplies
Light dimmers
Hair dryers
Computers
Variable frequency drive units found on many of the furnaces built today. (Controls blower motor speed)
Dual wattage portable electric space heaters.
CFL and LED lights
Electronic ballasts
//
PS Audio power regeneration units.
Curious, have you ever checked if the outputs of the two units are in phase with one another? If you have a multi meter measure the voltage from the hot contact from one of the output receptacles on one units to the hot contact of an output receptacle on the other unit. If the outputs of the two units are in phase you should measure zero volts nominal. If out of phase you will measure 240Vac nominal.
//
Sub Panel.
Don’t use it to feed your audio equipment. The wire feeding the panel is too small. Use the main electrical panel.
http://www.p3-inc.com/images/grounding_for_pq_wp2016_p3.pdf
.