If you can use NM-B cable (Romex is a trade name) that seems to be the most popular. If you use NM-B cable have the electrician use plastic outlet boxes instead of steel boxes if possible.Should read:
Have the electrician keep the NM-B cables separated from one another when parallel to one another for long distances. Also try to keep them from other parallel branch circuits after he gets out the the electrical as soon as possible, within reason. Especially lighting branch circuits. (Dimmers, electronic ballasts, CFL lamps, LED lamps. All radiate RFI harmonics through the air.)
Also try to keep them from other parallel branch circuits after he gets out *of* the electrical *panel* as soon as possible, within reason.
.
Because of the 75ft length of the branch circuits I would use #10awg solid core copper wire. Don’t let the electrician talk you out of it. Don’t let him try to talk you out of using solid core wire either. He will tell there is no difference between solid and stranded wire. LOL, for him there is, Stranded is easier to work with. Expect to pay a slightly higher labor cost though.Should read:
He will tell *you* there is no difference between solid and stranded wire.
.
If conduit is used ask the electrician if he will twist the hot and neutral conductors together the entire length of the conduit run and pull the insulated equipment grounding conductor in the conduit along side the hot and neutral twisted pair. If he can not or will not, then there is a very good chance, high probability, with a 75ft run of conduit with the hot and neutral wires pulled loosely in the conduit with the equipment grounding conductor wire you will have ground loop problems, 60Hz hum.
I should have added, though I have read the benefits of twisting the hot and neutral conductors together prior to installing them in an empty conduit it may not meet electrical code requirements. I have looked at the NEC and have not found anything that directly prohibits twisting the hot and neutral conductors together and then pulling the twisted pair in a conduit. That doesn’t mean it isn’t in there somewhere though. Bottom line, is it allowed by the AHJ (Authority Having Jurisdiction) electrical inspector in your area? He/she has the final say. Period.
Jim