@jea48 Funny you should mention socket outlets, I just changed my socket outlet from a generic to a Furutech outlet (audiophile brand). When I opened up the original socket, there were only 2 connections made with no ground. That is how I know there is no ground. I looked in the socket for a ground wire and did not find one, so when I swapped out the outlets, I simply mirrored the previous installation - no ground wire to connect.
Just because there was not a ground wire in the box that does not mean the equipment ground is not present. If rigid conduit was used per NEC code the conduit is an acceptable grounding means. The conduit is the equipment grounding conductor. (Of course the rigid conduit must be electrically continuous from the outlet box all the way back to the electrical panel. It can be connected to other metal boxes and conduit bodies in it’s travel.)
Note. Just because NEC allows rigid conduit to be used as an equipment grounding conductor that does not mean your city electrical inspection department does. The AHJ (Authority Having Jurisdiction) has the final say.
Buy one of these.
https://www.homedepot.com/p/Power-Gear-3-Wire-Receptacle-Tester-50542/206212329?cm_mmc=Shopping%7cTH...
It will tell you if the receptacle outlet is grounded and if the Hot and neutral AC polarity is correct. It will not tell you the conductivity integrity of the equipment grounding conductor to carry ground fault current back to the electrical panel in the event of a ground fault event though. Not matter if the conduit is used as the equipment grounding conductor or a ground wire is used.