Dealing with a power amp that need 20A connection


I just bought a used Audio Research power amp without knowing it needs 20A connection.
When I received the amp, there was no power cable included, and I've found out that the amp has a connection that I've never seen before. I thought it might be for 250 Volt, but later found out that this amp needs a special power cable with C19 type female connector and it has to be 12 AWG and 20A.
So, I ordered a 20A 12AWG power cable and a PS Audio power receptacle that supports 20A male connector type.
After reading a few more articles on 20A power amp, I may also need a 20A circuit breaker. The problem is, the circuit breaker for the audio room is 15A. Does it mean that I need a new breaker with 20A to use the amp?
What a hassle.
The seller did not mention anything about the cable power requirement and I assumed that it was included, but the seller didn't seem to have known anything about this amp. 
So, installing a new circuit breaker is something non tech people can do? If not, how much would I need to spend for professional job?
Would it be just OK to use 15A circuit breaker for the amp as long as I use 20A 12AWG power code and don't turn the volume much high?
Thx advance for your input.
ihcho
It would help if you gave us the Model number of the ARC amp.

As for tripping the 15 amp branch circuit breaker. If the breaker trips it won’t be while listening to music even at a high volume level, jmho. If it trips it will be when the amp is first turned on. Can the breaker handle the inrush current needed to charge the caps in the power supply. Just a guess ARC designed a soft start circuit to limit inrush current.

Other factors to consider is what other loads are connected to the 15 amp branch circuit? Also the electrical panel/breaker manufacturer and the age of the breaker.

As for how the amp will sound connected to the 15 amp branch circuit?
The wire gauge is more than likely #14awg copper. How many outlets are connected to the branch circuit? What other loads are connected to the branch circuit? Any lighting loads? CFL or LED? Dimmers? What is the wiring method used for the wire connections inside the wall outlet boxes? Pigtailed and then connected to the outlets, or, the outlet terminals were used, daisy-chained, to make the in and out connections of the Hot and neutral conductors? What is the distance, length, of the branch circuit wiring from the electrical panel to the wall outlet the amp will plug into? A little hard to figure that one. Add fudge for up, down, and around. Last but not least the age and condition of the wall receptacle outlet. Poor contact plug retention pressure will greatly degrade the sound of the amp.

Good chance you may want to hire an electrician to install a new 20 amp dedicated branch circuit for the amp. I would recommend #10awg wire. #12awg is bare minimum per NEC for a 20 amp circuit.
Jim
You need a 20 amp line run to the amp. It probably should be a dedicated circuit , that is just for the amp. The C19 power cable is the standard for 20 amp equipment. Put all your other equipment on the existing 15 amp circuit. 
No one 'needs' as "required" a separate 20 amp for the amplifier, unless they play LOUD.. it might be a something to upgrade to in the future... but not a requirement
elizabeth
No one 'needs' as "required" a separate 20 amp for the amplifier ...
The OP didn't mention what ARC amplifier he owns. Some amps do require a 20A line.