"it's definatly a safer system as you would not get shocked unless you touched both legs at the same time."
Not if you wired the secondary of the xfmr correctly. The center point of the xfmr should be bonded to the main service grounding electrode system. Thus this is a grounded conductor. This is also the point in which the equipment grounds of this new AC derived system will tie to. You will have 60V to ground from either one of the two hot conductors of the 120V system.
http://www.peavey.com/support/technotes/soundsystems/acpowerdist.cfm
http://www.circumtech.com/development/technology/balancedpower/liftingthegroundingenigma
What type of receptacles did you use? Isolated grounding type?
Not if you wired the secondary of the xfmr correctly. The center point of the xfmr should be bonded to the main service grounding electrode system. Thus this is a grounded conductor. This is also the point in which the equipment grounds of this new AC derived system will tie to. You will have 60V to ground from either one of the two hot conductors of the 120V system.