"The input has been config for 240v in as thats what my apc runs on, and output taps 5 and 8, this system was made to be tough,mainly becaus of the sunfire high current draw."
"apc", Apartment
"taps 5 and 8" >>> #5 = 0, #8 = 115V output.
=============================================
"The input has been config for 240v"
Then #2 & #3 tied together? With the 240V supply connected to terms #1 & #4?
=============================================
2000VA
Agreed more than likely xfmr is to small.
Max safe load of xfmr 2000 x 80% = 1600VA
Check the output voltage of the xfmr with the load connected. The load being the Sub
Jim