Jea48, CJ350 stock PC comes with a 15amp plug.
It doesn't make sense. As far as I understand it , shouldn't equipment with need a 20amp IEC comes with a 20amp plug which rightfully should be connected to a 20amp dedicated circuit with 20amp circuit breaker to maximise whatever current the equipment need?
I assume the CJ amp is UL and or CSA listed. If so the equipment was tested and found that it did not exceed an FLA, (full load amps) of more than 12 amps. That meets the minimum plug that can be used on the cord of the equipment.
CJ could have supplied a cord with a 20 amp plug but imagine the complaints from the consumer. The damn thing won't plug into my
Oyaide receptacle.....
You the user can step up to a power cord that has a 20 amp plug if you wish. What you should do is make sure the conductor, wire, in the cord is at least #12 awg gauge. Make sure the IEC female connector fits tightly into the male connector on the back of the Amp. Poor contact pressure causes arcing. Arcing causes noise as well as heat and voltage drop.
Also for your amp a dedicated 20 amp circuit with a good quality receptacle. Just a note here on receptacles. The guts inside a good quality recept use the same 20 amp rated contacts be it 15 or 20 amp..... Only the faceplate is different. It's an NEC safety thing as I described in an earlier post.
Wire size for the 20 amp branch circuit? Minimum of #12 awg. In your case if the total run is more than, say 30' to 40' I would have installed #10 solid wire. Jim