Electrical panel : Ground/Neutral bus bar question


Hi,

In CH type panel CMBE4242B200BTS ( main bus is Copper) , I am trying to replace AL ground/neutral bus bar with

http://www.dinrailwiringduct.com/12-inch-long-ul-listed-copper-ground-bar-or-earth-bar-w-screws-included-and-pre-inserted/

My concern is, most of the Eaton mounting holes are 1-3/4" whereas the Ilsco mounting holes are 2.566".

Should that be concern ? Can I use wire hole as mounting holes ( whichever is aligned to panel holes) ?

Are there any other options for copper Ground/Neutral bus bar ?

Do you guys think if it worth pursuing changing Ground/Neutral bus bar to copper from Aluminum ?

Thanks
128x128diwakarv
Thanks Cdrc. I am using copper SE cable & 4 AWG solid copper GND wire terminated to 8 feet solid copper bar ( about 50 feet from Main panel) and to water mains. I have bought Cardas in wall AC for two dedicated circuit, 10/2 romex for subwoofer, 10/2 as spare. My outlet are Oyaide R1 with wallplate. Lugs in my meter are copper, not aluminum ( special order from Flexcenter).

I am sort of disappointed that I couldn't get all copper panel anyways , knowing that AL is just 40% conductive to copper.

I wish I could post picture on Audiogon to expain my situation further. Lug for GND ( where 4 AWG attaches in the panel) can accept copper and AL ( it is 6061-T6) and GND strap which connects to GND/NEUTRAL bus bar (BSSUSE Bonding Strap) is also 6061-T6. Ideally, I should be able to replace GND/neutral bus with N174 copper bar.

Again since bonding strap is also 6061-T6 ( Tin plated), copper bar screw to it, should not cause any harm. I am bit skeptical/reluctant after Jea48 comments.
Here is picture of the panel that I discussing about
https://www.flickr.com/photos/131393447@N08/17442124326/in/shares-S47X7U/
In my opinion ( as an circuit engineer), if the resistance is introduced in source path ( breaker contact, OR main distribution bus) or return path ( to GND via Ground/Neutral AL bus), it is bad. It is definitely worse in return path since all the current from refrigerator/washer/dryer/oven and all electrical appliances are dumped into this. Having this path as AL instead of CU is not the best.
Sure, according to NEC perspective, it is enough to carry current ( whatever rating it is designed for ) but it is definitely not desirable from audio application.
This is response that I got from eaton

My question

Hi,

Can I replace neutral/Ground (Tin plated aluminum) in
CMBE4242B200BTS panel with ILSCO copper bars ?

Thanks

Reply from Eaton

Since it’s a service entrance panel, the neutral/ground is bonded, so I don’t see any issue with changing to a different ground bar. However if any inspector noticed the difference and called you out on it, we don’t have anything official documentation to back you up in doing this. So I would suggest you hold onto the original neutral/ground in case the inspector says you can’t change it.
Since it’s a service entrance panel, the neutral/ground is bonded, so I don’t see any issue with changing to a different ground bar.


Do you understand what the guy means when he says the neutral/ground bar is bonded? What that means, and yes that is the case with the meter/Load Center combo unit you bought. The service neutral conductor is bonded, connected, to the meter socket steel enclosure. Inside the Load Center electrical panel the neutral/ground bar is bonded, connected, to the steel metal enclosure again. Yes that is the way it is done. Even where the meter socket is separate from the electrical panel it is Bonded in the same way. (At the meter socket and again at the electrical panel.)

So can / does the unbalanced load current travel on the steel enclosure between the two bonded points as well as the AL bus between the meter socket main service bonded neutral connection and the bonded neutral bar connection? You bet.

What you should have asked the guy, is the AL bus that connects the main service neutral conductor in the meter socket to the neutral/ground bars in the electrical panel made of 6061-T6 AL alloy? That is what you need to bolt a copper neutral/Grd bar to the AL bus. If the AL bus is not 6061-T6 AL alloy and you connect the AL bus to copper the connection in time will fail. Will the bonding screws/straps/steel enclosure carry the unbalanced load current back to the utility transformer? ya, I guess.... Will the bonding screws connections to the main service neutral conductor keep the L1 to neutral and L2 to neutral 120V nominal voltage stable? Hopefully.... Will the total resistance of the bonding screws and steel enclosure be less than the AL bus that connects the main service neutral conductor to the 6061-T6 AL alloy neutral/Grd bars? I doubt it...
.