I assume, though, that modern code doesn't permit installation of conduit containing only two conductors. Am I correct about that?
02-11-14: Almarg
Al,
As for NEC 2011 Code, Rigid, IMC (intermediate Metal Conduit), EMT (thin wall), are reconized as an equipment grounding conductor.
Flexible metal conduit 6' or less in length is also acceptable for use as an equipment grounding conductor provided the connectors are Listed for use as equipment grounding means, and the branch circuits is 20 amps or less.
Remember NEC Code is bare minimum. The AHJ (Authority Having Jurisdiction) in the area a person resides may not allow the above metal conduits to be the sole equipment grounding conductor. The AHJ may require an equipment grounding wire to be installed in the conduit with the other branch circuit wires.
The problem I have with using any metal conduit for the equipment ground is the continuity integrity of the couplings and connectors to maintain a good conductive electrical connection over the passage of time. Not to mention how well the conduit installation, fittings tightness, was to begin with.
As for the white paper....
I was glad to see actual testing done for an equipment grounding conductor sharing the same raceway or cable as the current carrying conductors of a branch circuit.
I always thought a voltage could be induced from the current carrying hot and neutral conductor over onto the equipment grounding conductor on a long branch circuit run. We now know why many audio enthusiasts recommended using NM-B cable, (Romex is a Trade name of NM-B), for audio equipment branch circuits.
One thing for sure, conduit runs where the wire is installed after installation is the worst thing for audio. And to repeat what I have said in the past, dedicated branch circuits should not share the same raceway, conduit, with other branch circuits.
For those out there that have to use conduit I suggest MC cable with aluminum armor and solid core conductors. MC can be bought with solid or stranded wire conductors.
MC Cable http://www.afcweb.com/product-category/mc-metal-clad-cables/
.
.
**Just an added note.
Old homes built before around the middle 1950s and earlier may be wired with old BX cable wiring. Construction of the cable is 2 insulated cloth covered conductors with a steel spiral armor cover around the conductors.
The receptacles back then were the old 2 wire type.
The armor on this BX cable should not be used as an equipment grounding conductor. Not only is the steel armor not an effective ground fault path for fault current, neither is the electrical connection of the BX to box connectors.
NEC 1959 Code required AC/BX cable to have a continuous bonding strip installed under the armor so the cable could be used as an equipment grounding conductor. Just guessing the BX to box connectors were still the same old connectors. By NEC 1962 Grounding type receptacles were required.
Here are a couple of Links.
http://www.inspectorsjournal.com/forum/topic.asp?TOPIC_ID=10144
http://www.dslreports.com/forum/r26797846-using-BX-cable-as-a-ground-
Jim