My new apartment has no 3 prong plugs with ground


Just moved, my new apartment has no three-pronged plugs within any distance of my living room. Only old 2 prong plugs with no ground.
I have been using a 3-pronged converter for now.

Anyone think this will effect my system?
Danger in damaging something?
Should I chase new wires up and put in a new outlet?
ejs811
The house is a duplex, our floor has 100 amps: 2 X 30 and 2 X 20, people below us have 140 for some reason. Maybe its their new kitchen. Looks like the dryer is on its own 30amp wring which is good.

I screwed the cheater into the center screw of the faceplate. Not going to mess with anything for now, the wiring is a nightmare in the basement.
Speak to landlord to go with the building CODE and to replace/rewire them ALL at once. Calling building inspector once in a while will stimulate the landlord's speed of action.
The house is a duplex, our floor has 100 amps: 2 X 30 and 2 X 20
09-09-12: Ejs811


Ejs811,

Sorry it doesn't work that way....
The size of the service is not determined by adding up all the plug fuses amp ratings.

At best I would guess the service feeding your apartment is 60 amp. At worst 30 amp.
.
Ejs811, Look at your electrical panel. Sometimes it will state the capacity of your electrical service. Or, you can set up your gear and not worry about it. The only thing possibly drawing a lot of current is your amplifier and it depends on the load presented by your speakers and the volume you listen at. I would not count on your landlord rewiring any time soon.
There will be two mains fuses, at the top of your electrical panel. Read the sizes on those, to determine how much amperage is available, per phase. Outlet boxes in older homes ARE NOT USUALLY grounded. Especially if the wiring is knob and tube. Unless the wires were run through metal conduit(EMT), metallic liquid-tite, Bx cabling or have a third ground conductor to the box; it is NOT grounded. Grounding(running a pigtail) to the new outlet to an ungrounded box would be a waste of time/effort. Besides; the ground terminal on grounded outlets, is already grounded to the box through the mounting tabs/screws.