I didn't even realize that the ground wire was supposed to return to connect to the main house panel!!Yes it does, as per NEC.
I thought we were going to run a ground wire from the sub-panel via a #6G bare copper wire to an 8'-10' pole hammered into the ground at least 8' from the garage and that was THE ground..Have your electrician read NEC 2005 250.54 Supplementary Grounding Electrode. Page 70-103
Do I still do that, even with the #6G returning to the main house panel [underground and in the soffit] along with the 2 hots and 1 neutral #2G's? BTW, if I use a PVC tube to encapsulate the underground wires will that be a different type of wire/can it be the same as the "in-house/soffit type" as compared to an "underground feeder cable"? I was checking prices on #2AWG copper cable and we're up to at least $2.50 per foot! Does that mean 65' + 45' = 110'x3 runs (2hot,1neutral) for a total of 330' x $2.50ea = $825 plus the 110' of #6 ground @ $xx? per foot? WOW...
I said it would cost you an arm and a leg.....
You could use aluminum. You would need to increase the size to #1 awg, and the equipment ground wire to a #4 awg.
The wire from your main electrical panel in your home to a junction box mounted on the house above the earth could be insulated THHN/THWN copper installed in 1 1/4" EMT metal conduit. You could use 1" EMT per code but trust me it is a bitch pulling 3 #2 and a #6 in 1".... From the JCT box through the earth to the new sub panel XHHW insulated copper wire in
1 1/4" PVC conduit.
Also, when you say the dedicated branch circuit will have 1hot,1neutral,1gnd... you are referring to the individual wire of 12/2 or preferably 10/2 Romex which attaches to the outlet? When you say "No sharing of neutral" what does this imply?
Multi wire branch circuits.
You can have two 120V separate branch circuits sharing the same neutral.
Each Hot conductor must be connected to opposite Lines, legs, in the sub panel. One on L1 the other one on L2. With this wiring configuration only one neutral conductor and one equipment grounding conductor are required. Two separate circuits..... But not two dedicated circuits.
I was thinking of running 2 x 5362 Hubbels next to each other 9for a total of 4 plug in points0 per 20A dedicated line...Sounds fine. Many will recommend using plastic rough-in boxes instead of metallic.