Grimace,
When you sent the amp to Cary did you also send along the power cord that is used on the amp?
How about the repair shop. Did you take the power cord with the amp?
>>>>>>>>>>>
I assume you have a multimeter.
(1) With the amp turned on measure the AC voltage at the wall duplex receptacle.
(2) With nothing plugged into the duplex receptacle measure the AC voltage.
(3) Check the AC voltage from the hot contact to the equipment ground contact.
(4) Check for AC voltage from the neutral contact to the equipment ground contact...
Make sure the meter is set to AC auto.
Make sure both meter test probes are making good contact.
Post back the measurements.
.