Lissnr,
Where does it say the PS 1200 is a surge protector?
The video says the unit is UL approved. UL 1449 - 3rd addition?
The video with the motor mounted on the board is very misleading.
A squirrel cage induction motor without a connected loaded will have a very poor PF (power factor). The closer the motor is loaded to its rated HP (horse power) the more efficient the motor will be. There in higher PF.
It appears the PS 1200 is nothing more than an AC capacitor that when connected across the AC mains will raise the mains line voltage somewhat.
In the case of a squirrel cage induction motor operated within the motor nameplate data specs an increase in line voltage will result in a decrease in current draw, amps.
P = E x I
P = power measured in watts
E = voltage
I = amps
The Power Utility company meter measures watts consumed. That is why it is called a watt hour meter.
As a residential power user I see no savings gain from using the PS 1200 unit.
Sorry.......
.
Where does it say the PS 1200 is a surge protector?
The video says the unit is UL approved. UL 1449 - 3rd addition?
The video with the motor mounted on the board is very misleading.
A squirrel cage induction motor without a connected loaded will have a very poor PF (power factor). The closer the motor is loaded to its rated HP (horse power) the more efficient the motor will be. There in higher PF.
It appears the PS 1200 is nothing more than an AC capacitor that when connected across the AC mains will raise the mains line voltage somewhat.
In the case of a squirrel cage induction motor operated within the motor nameplate data specs an increase in line voltage will result in a decrease in current draw, amps.
P = E x I
P = power measured in watts
E = voltage
I = amps
The Power Utility company meter measures watts consumed. That is why it is called a watt hour meter.
As a residential power user I see no savings gain from using the PS 1200 unit.
Sorry.......
.