Here are the NEC requirements. You're not running balanced power everywhere, just the audio system, right? At any rate you might want to read all the way through:
NEC 647, which defines the requirements for balanced power systems, places some important restrictions on both their installation and use.
1. Conductors must be sized so that the IR drop does not exceed 1% of the line voltage under a load equal to 50% of the branch circuit current rating, and so that the
combined IR drop of the feeders and the branch circuit wiring does not exceed 2%.
2. A dedicated Equipment Ground conductor must be run to all equipment and each receptacle.
3. All receptacles must be protected by a GFCI.
4. The neutral must be bonded per NEC 250, and must also be connected to the grounded conductor of the circuit that feeds the system.
5. Balanced power systems are restricted to industrial and commercial occupancies.
6. All outlets shall have a unique configuration and must be identified using specific language called out in NEC 647.7.
7. There must be a receptacle having a grounded circuit conductor (i.e., conventional unbalanced power) within 6 ft of each receptacle for the balanced power system.
8. All lighting fixtures connected to balanced power must be specifically rated for 60/120 VAC balanced power, must have a disconnecting means that interrupts all
ungrounded conductors, and must be permanently installed.
9. Isolated ground receptacles are permitted. Balanced power systems are expensive, and their noise reduction capability is limited to about 10 dB. Isolated ground systems are generally a far more effective and less costly solution.
This might be old hat for you, but that final point is where I was going...