That is why NEC Code as well as UL requires the output of the balanced power system to be GFCI protected. Any imbalance of either hot conductor to ground will cause the GFCI to trip open. As little as 5 or 6 milliamps of ground fault current to ground will trip the GFCI open. Wonder how many guys here who wired their own balanced power systems are using a GFCI on the output of the transformer?
It should be noted that a GFCI will not operate as designed when connected to the output of an "Isolated Power System" (Floating above ground). An equipment ground is not needed for a GFCI to operate as designed, but it must be connected to a "Grounded AC Power system" to operate as designed.
That is why NEC Code as well as UL requires the output of the balanced power system to be GFCI protected. Any imbalance of either hot conductor to ground will cause the GFCI to trip open. As little as 5 or 6 milliamps of ground fault current to ground will trip the GFCI open. Wonder how many guys here who wired their own balanced power systems are using a GFCI on the output of the transformer?