Installing an AC Grounding System, Need Advice


Later this week, my electician will begin work on my electric project, which will involve the installation of a 7.5kVA isolation transformer that will be fed from a separate meter tap. The isolation transformer will be installed in front of a new dedicated circuit panel that will house the dedicated circuits that will feed my listening room. All the dedicated circuits will be fed from the same side of the bar in the new panel in order to maintain consistent phase.

As Sean has advised in a separate thread, I know it is important that I check - and upgrade as necessary - the ground for my AC system. (My house was built in the late 1950s, and, from the looks of things, not much has been done since that time to upgrade the electric service. So I am nearly certain that I will find the grounding system leaves much to be desired.) I also know from discussion in various other threads that it is important for the entire electrical system in my house to share a common ground. So I expect that I will need to upgrade the grounding system into my main circuit panel and then tie the isolation transformer and the new dedicated panel back to that same grounding system.

The work on my house is being performed by a qualified electrician, but, as I have noted in other threads, I would like advice on the audiophile details that can make a difference in the sound (in this case, the noise floor) of my system. Perhaps I should also mention that my plan involves installing a separate dedicated circuit for each of my seven components. Given that this sort of a set-up is more prone to ground loops, I am interested in advice regarding how to avoid them with this set-up.

With that as background, would any of the resident experts be willing to share with me the details of how to install a high quality grounding system for my AC power? I would appreciate as much detail as possible regarding the materials to use as well as installation advice.

I have read some advice in other threads recommending two separate copper grounding rods driven into the ground relatively close to each other with a weather-proofed connection between the two rods that is, in turn connected to the electrical system. I have also seen some advice that I believe involves wiring one of these connected ground rods to the main house circuit panel and the other connected ground rod to the audio portion of the system (i.e., in my case, the isolation transformer and the new dedicated circuit panel). Please let me know if this is headed in the right direction and, if so, please help me to fill in some details (dimensions of the copper, advice on how to drive it into the ground without mangling it, distance between the redundant rods, any other details you see fit).

As always, thanks for your help and patience.
cincy_bob
Jea48, thanks for all your input. It is really valuable to me as I lack personal expertise in this area. Here are some answers to your questions:

1. Soil and Moisture - As my user name implies, I live in the Cincinnati, Ohio area. Our soil in this area involves a lot of clay. We tend to have normal midwestern weather with a fair amount of precipitation yearound but occasional droughts in the summer months. Let me know if additional information would be helpful in this area.

2. Isolation Transformer - My isolation transfomer is an MGE Topaz isolation transformer that is described in the following web link:

MGE Topaz 100 Installation and User Manual

This web link will lauch a pdf file that contains the full user manual for my isolation transformer. The specifications for the unit are contained on page 11 of the document. My unit is model no. T-100H-7500. It is a hardwired 7.5kVA transformer (see pg. 12 for the specifications of the various model numbers).

The unit provides 140dB of common mode noise attenuation and 65dB of normal mode noise attenuation. I believe the transformer also provides the electrostatic shielding that you mentioned in your latest post.

By the way, my use of the word, "taps," simply shows my inexperience with the subject matter. I had no technical basis for the use of that term.

Based on the advice in your latest post, it sounds like I should use the transformer to step down the 240V primary voltage to 120V at the output stage.

It would be a lot of help to me if you would explain a bit more to me about the primary and secondary grounding electrodes in my system. If I understand your posts to date, you are suggesting that, to comply with code and safety standards, the grounding electrode on the primary stage of the isolation transformer must be tied back to the grounding system at my main electric panel in my house (i.e., the clamp that is attached to my water pipe service where the service enters my house).

When you refer to the secondary grounding electrode, are you referring to a second ground connection from the secondary side of the isolation transformer? Did I understand your first post in this thread to suggest that it is best to have a ground for this secondary side of the transformer that is independent of the water pipe ground that is used as the primary ground for my electric system? I have seen a lot of cautionary advice about the use of two separate grounds within an electric system. The cautionary advice seems to say that it is never acceptable to have two separate grounding systems for two parts of an electrical system. Can you clarify this part for me?
The feed from your existing service that will feed the 7.5 kva xfmr will be 2hots, 230v,+ 1 equipment grounding conductor. The equipment grounding conductor will bond, connect, to the case of the xfmr. This ground is for the xfmr only.
Think of this ground as a safety ground.

When you install a transformer of the size you are using you are creating basically a new service. That means the 120 volt secondary side of the xfmr must follow certain safety guidelines to meet the NEC and your local city codes. That is why you need to connect one of the 120 volt leads of the secondary of the xfmr to the neutral bar in the new electrical panel that will be installed. This wire will become the "grounded conductor", the neutral. From this neutral bar a #6awg cu ground wire will run to the main incoming water line ahead of the water meter. This wire is called the "grounding electrode conductor". The wire attaches to the water pipe with an approved water pipe ground clamp. The water pipe is now called the "grounding electrode". This is the primary "grounding electrode" and "grounding electrode conductor" I spoke of in my earlier post. The connection at the main water line is the common ground point that ties your new 120v service to your existing house service.They will both be on the same ground plane. Now back to the neutral bar in the new panel. The electrician will install a supplied bonding screw through the neutral bar into the panel enclosure. Now for the secondary grounding electrode conductor that will go outside to the second "ground electrode" you choose to use. This second ground also connects to the neutral bar in your new panel.The new panel will have two earth ground system connections. Primary,water line ground electrode, and secondary, outside new earth ground electrode. The neutral bar is a Star grounding point now. By the way in your area your water line is probably down 4 to 5 feet deep because of frost. Buried in moist clay the distance, length, from the house to the main trunk connection and beyond.
Back to that neutral bar in the new panel. This bar is where all the new branch circuit neutral wires and equipment grounding wires will terminate...Nec says the neutral shall be bonded to ground at the first point of attachment or disconnecting means and at no point there after. That is why sub panels have seperate equipment ground bars. This is not a sub panel. In this new panel the neutral wires and ground wires share the same connection bar, called the neutral bar. NEC also says the max resistance between the neutral, grouned conductor, and the equipment grounding conductor measured at the receptacle shall not exceed 3 ohms. Also If you can keep the new panel fairly close to the new branch circuit receptacles thats also agood thing.

I have tried to do a better job of explaining things. This is the simple part. Putting it all together in a neat and workman like manner is the tough part. Local codes can vary. Your electrician should know the code of your area.
Cincy: You really can't do a free, engineering project via an audio Forum. That's a bit much to expect, both financially and even more importantly, from a liability standpoint. You are very bright, curious, and well spoken, but, respectfully, and I'll buy the first beer - y'all are drifting into a real project. And, respectfully, if we don't know that ground rods come in 10 ft lengths, and that driving one takes a specialized tool, and is the ultimate in apprentice physical labor, and that there are a ton of NEC requirements to be met, well...

Saying that you may want to consider engaging a freelance (not an engineering company) registered electrical engineer to prepare several drawings on what you wish to do. You can verbalize your electrican through it, but, that is always poor practice. That includes an as-build of your entire home system. Expensive, but hand waving a Journeyman electrican will burn up a stupid amount of hours; and here in N. CA, the billing rate will be about $80/hour.

Not a shareholder, employee, sales rep of any mentioned product. The XIT system is a large, hollow ground rod packed w/ trick material. It is vented at the top to absorb ambient humidity, thusly maintaing a very low impedance with the contacting soil throughout the year despite weather conditions. It is used by Honeywell for their DCS (Distributed Control Systems) in their localized Remote Instrument Enclosures handling plant control of digital inputs/outputs and analog signals in the milliamp level. It is installed in at least one Chevron refinery in California.

It also is, possibly, stupid overkill for a residential app., but in this day and age when 6loons is reviewing new-car priced transports/DAC's, I'm lost...

If your curent system is in good condition, and has a measured reasonable impedance, I wouldn't loose sleep on this...
Shasta, about a month ago, I hired a registered electrical engineer to develop drawings for the modifications to my residential electrical system. What I have been doing in this forum is educating myself so that I can raise the right topics with - and ask the right questions of - my electrical engineer and my electrician.

The service drawings for my system do not contain any detailed specifications for the grounding of the new circuit panel. Without the aid of this forum, I would not have known that there was any alternative to simply grounding the new panel back to the incoming water line that currently serves as the grounding electride for my electric system. And, without any discussion of the topic with my electrician, I am sure he would have opted for this single ground without any discussion and without me being aware of any alternative for a secondary ground. The education Jea48 has provided me regarding the option of installing a secondary outside new earth ground electrode allows me to have an intelligent conversation with my electric professionals that I could not otherwise have even initiated.

Jea48, thanks very much for all the information you have shared. It is very helpful to me and will significantly enhance my ability to communicate with my electrical engineer and electrician.
I'd check out www.equitech.com. They're the people into balanced power; however, they also have different articles that can be downloaded via computer. One of these articles is "setting up an a/c ground." I used one 10' 5/8" copper ground rod. If you use two, they need to be separated by at least 8'. As for putting the ground rod into the ground... Use water. Slowly dribble it into the hole that the rod is making, as you plunge it up and down. The pressure of the rod tip--(like a high heel shoe-pressure per square inch, ouch!), and the water at the hole's developing surface will cut through the dirt in no time. Be careful with that project. I've read multiple grounds can be dangerous. Hope all this helps. Good Listening!