The feed from your existing service that will feed the 7.5 kva xfmr will be 2hots, 230v,+ 1 equipment grounding conductor. The equipment grounding conductor will bond, connect, to the case of the xfmr. This ground is for the xfmr only.
Think of this ground as a safety ground.
When you install a transformer of the size you are using you are creating basically a new service. That means the 120 volt secondary side of the xfmr must follow certain safety guidelines to meet the NEC and your local city codes. That is why you need to connect one of the 120 volt leads of the secondary of the xfmr to the neutral bar in the new electrical panel that will be installed. This wire will become the "grounded conductor", the neutral. From this neutral bar a #6awg cu ground wire will run to the main incoming water line ahead of the water meter. This wire is called the "grounding electrode conductor". The wire attaches to the water pipe with an approved water pipe ground clamp. The water pipe is now called the "grounding electrode". This is the primary "grounding electrode" and "grounding electrode conductor" I spoke of in my earlier post. The connection at the main water line is the common ground point that ties your new 120v service to your existing house service.They will both be on the same ground plane. Now back to the neutral bar in the new panel. The electrician will install a supplied bonding screw through the neutral bar into the panel enclosure. Now for the secondary grounding electrode conductor that will go outside to the second "ground electrode" you choose to use. This second ground also connects to the neutral bar in your new panel.The new panel will have two earth ground system connections. Primary,water line ground electrode, and secondary, outside new earth ground electrode. The neutral bar is a Star grounding point now. By the way in your area your water line is probably down 4 to 5 feet deep because of frost. Buried in moist clay the distance, length, from the house to the main trunk connection and beyond.
Back to that neutral bar in the new panel. This bar is where all the new branch circuit neutral wires and equipment grounding wires will terminate...Nec says the neutral shall be bonded to ground at the first point of attachment or disconnecting means and at no point there after. That is why sub panels have seperate equipment ground bars. This is not a sub panel. In this new panel the neutral wires and ground wires share the same connection bar, called the neutral bar. NEC also says the max resistance between the neutral, grouned conductor, and the equipment grounding conductor measured at the receptacle shall not exceed 3 ohms. Also If you can keep the new panel fairly close to the new branch circuit receptacles thats also agood thing.
I have tried to do a better job of explaining things. This is the simple part. Putting it all together in a neat and workman like manner is the tough part. Local codes can vary. Your electrician should know the code of your area.
Think of this ground as a safety ground.
When you install a transformer of the size you are using you are creating basically a new service. That means the 120 volt secondary side of the xfmr must follow certain safety guidelines to meet the NEC and your local city codes. That is why you need to connect one of the 120 volt leads of the secondary of the xfmr to the neutral bar in the new electrical panel that will be installed. This wire will become the "grounded conductor", the neutral. From this neutral bar a #6awg cu ground wire will run to the main incoming water line ahead of the water meter. This wire is called the "grounding electrode conductor". The wire attaches to the water pipe with an approved water pipe ground clamp. The water pipe is now called the "grounding electrode". This is the primary "grounding electrode" and "grounding electrode conductor" I spoke of in my earlier post. The connection at the main water line is the common ground point that ties your new 120v service to your existing house service.They will both be on the same ground plane. Now back to the neutral bar in the new panel. The electrician will install a supplied bonding screw through the neutral bar into the panel enclosure. Now for the secondary grounding electrode conductor that will go outside to the second "ground electrode" you choose to use. This second ground also connects to the neutral bar in your new panel.The new panel will have two earth ground system connections. Primary,water line ground electrode, and secondary, outside new earth ground electrode. The neutral bar is a Star grounding point now. By the way in your area your water line is probably down 4 to 5 feet deep because of frost. Buried in moist clay the distance, length, from the house to the main trunk connection and beyond.
Back to that neutral bar in the new panel. This bar is where all the new branch circuit neutral wires and equipment grounding wires will terminate...Nec says the neutral shall be bonded to ground at the first point of attachment or disconnecting means and at no point there after. That is why sub panels have seperate equipment ground bars. This is not a sub panel. In this new panel the neutral wires and ground wires share the same connection bar, called the neutral bar. NEC also says the max resistance between the neutral, grouned conductor, and the equipment grounding conductor measured at the receptacle shall not exceed 3 ohms. Also If you can keep the new panel fairly close to the new branch circuit receptacles thats also agood thing.
I have tried to do a better job of explaining things. This is the simple part. Putting it all together in a neat and workman like manner is the tough part. Local codes can vary. Your electrician should know the code of your area.