The earth does not possess some magical mystical power that sucks nasties from an audio system.
The main purpose for an electrical service connection to earth is for lightning protection.
You can fill your whole yard with driven ground rods if you like as long as they are all tied together and connect to one point to the main electrical service entrance neutral conductor.
NEC Code says the equipment grounding conductor for a sub panel shall installed in the same raceway, conduit, or cable assembly, as the feeder conductors feeding the sub panel.
The purpose of equipment grounding grounding conductor is provide a low resistance path for ground fault current to return to the source in the event of a ground fault event. THE EARTH IS NOT A LOW RESISTANCE PATH . When a sub panel is used the source is the main electrical service panel where the sub panel feeder equipment grounding conductor is connected to the service entrance neutral conductor. IF the ground fault current is greater than the breaker handle rating the branch circuit breaker in the sub panel will trip open breaking the ground fault circuit. IF the ground fault current leakage, due to a high resistance in the ground fault circuit, the circuit breaker in the sub panel just sees the ground fault current as connected load.
NEC code does allow an auxiliary grounding electrode to be connected to the equipment ground bar in a sub panel in addition to the feeder equipment grounding conductor.
IN ADDITION TO. NOT IN PLACE OF. I would not recommend it though. Lightning will travel through any path provided from the earth back to the earth. Especially a low resistance path.
Here is a great white paper for you to read.
https://centralindianaaes.files.wordpress.com/2012/09/indy-aes-2012-seminar-w-notes-v1-0.pdf
The main purpose for an electrical service connection to earth is for lightning protection.
You can fill your whole yard with driven ground rods if you like as long as they are all tied together and connect to one point to the main electrical service entrance neutral conductor.
NEC Code says the equipment grounding conductor for a sub panel shall installed in the same raceway, conduit, or cable assembly, as the feeder conductors feeding the sub panel.
The purpose of equipment grounding grounding conductor is provide a low resistance path for ground fault current to return to the source in the event of a ground fault event. THE EARTH IS NOT A LOW RESISTANCE PATH . When a sub panel is used the source is the main electrical service panel where the sub panel feeder equipment grounding conductor is connected to the service entrance neutral conductor. IF the ground fault current is greater than the breaker handle rating the branch circuit breaker in the sub panel will trip open breaking the ground fault circuit. IF the ground fault current leakage, due to a high resistance in the ground fault circuit, the circuit breaker in the sub panel just sees the ground fault current as connected load.
NEC code does allow an auxiliary grounding electrode to be connected to the equipment ground bar in a sub panel in addition to the feeder equipment grounding conductor.
IN ADDITION TO. NOT IN PLACE OF. I would not recommend it though. Lightning will travel through any path provided from the earth back to the earth. Especially a low resistance path.
Here is a great white paper for you to read.
https://centralindianaaes.files.wordpress.com/2012/09/indy-aes-2012-seminar-w-notes-v1-0.pdf