they want me to use a 30 amp single pole breaker so that my amp will run smoother, less heat, draw more current on demand, my sound stage will sound bigger and taller, and everything else, remember, all this is what krell swears too, they run my amp and the 750mcx amps on a 30 amp breaker thier at the factory, also,
11-11-14: Audiolabyrinth
Audiolabyrinth'
"They" told you wrong. First off the current carrying guts inside of a 20 amp breaker are the same as a 30 amp breaker. Only the trip unit settings are different. A 20 amp breaker will pass short bursts of current of over 100 amps all day long.
Per NEC Code a 20 amp NEMA 5-20R receptacle can only be connected to a 20 amp breaker. Minimum size branch circuit wire, #12 awg. The breaker size determines the size of the branch circuit. If # 10 wire is used the breaker still has to be a 20 amp if the receptacle is a NEMA 5-20R receptacle.
IF by chance the breaker is tripping occasionally on start up from high inrush current most breaker manufactures make a breaker with a longer lag time for high inrush current.
Example
>http://www.cesco.com/b2c/product/33471?gdftrk=gdfV25445_a_7c1847_a_7c7081_a_7c33471&gclid=CIurm-rygMICFY6EaQodj0MAvg
Two or more 15 amp NEMA 5-15R receptacles can also be installed on a 20 amp branch circuit. Per Code a 20 amp receptacle cannot be installed on a 15 amp branch circuit.