Audiolabyrinth,
Were you told by a Tech at Krell over the phone or through an email? Just guessing it was over the phone. See if the guy will send you an Email stating "Krell" recommends you use a 30 breaker to feed a 20 amp rated receptacle. Tell him you want to post it here on Agon.
As I said in my previous post the current carrying guts of a 20 amp breaker are the same as a 30 amp breaker, exactly the same.In fact they are the same as 40 amp breaker. Only the thermal and magnetic trip settings are different. And of course the number printed on the breaker handle.
As for the FLA rating of the Amp IF the amp is UL/CSA Listed the most continuous power the amp can draw is 16 amps, 80% of 20 amps. If it is over 16 amps the manufacture would then have to use a 30 plug mated to a 30 amp receptacle connected to a 30 amp branch circuit to get the UL/CSA Listing.
Were you told by a Tech at Krell over the phone or through an email? Just guessing it was over the phone. See if the guy will send you an Email stating "Krell" recommends you use a 30 breaker to feed a 20 amp rated receptacle. Tell him you want to post it here on Agon.
As I said in my previous post the current carrying guts of a 20 amp breaker are the same as a 30 amp breaker, exactly the same.In fact they are the same as 40 amp breaker. Only the thermal and magnetic trip settings are different. And of course the number printed on the breaker handle.
As for the FLA rating of the Amp IF the amp is UL/CSA Listed the most continuous power the amp can draw is 16 amps, 80% of 20 amps. If it is over 16 amps the manufacture would then have to use a 30 plug mated to a 30 amp receptacle connected to a 30 amp branch circuit to get the UL/CSA Listing.