I use an isolation transformer (medical grade) from the wall before my Shunyata Triton. It greatly improves the sound of the Triton vs. taking the Triton directly from the wall.
09-20-14: Sabai
Medical grade? I assume the secondary of transformer is floating above ground, is that correct? In other words the two output leads of the secondary are Hot ungrounded leads. Neither lead has a reference to ground. One lead was not intentionally connected to ground making it the neutral conductor thus making the new separately derived power system a "Grounded AC Power System".
NEC calls this type of power system an "Isolated Power System".
If your medical grade isolation power transformer is indeed operating as an Isolated Power System You will not read a true 120V reading from either contact of the receptacle to ground. Danger Will Robinson!